Are you replacing an existing water heater? If so, what was done with the old water heater's valve? Do you have a drain pan, and if so how does it drain? I have seen many P&T valves drain to the pan as a last resort, so I think it's acceptable, although not ideal.
I assume you're on a slab, or you could just drill through the floor and route your drain pipe out through the crawl space and through the curtain wall.
From what I found by Google, it appears that international building code does not allow venting to a sewer system.
504.4 Relief valve. All storage water heaters operating above atmospheric pressure
shall be provided with an approved, self-closing (levered) pressure relief valve and
temperature relief valve or combination thereof. The relief valve shall conform to
ANSI Z21.22. The relief valve shall not be used as a means of controlling thermal
expansion.
504.4.1 Installation. Such valves shall be installed in the shell of the water
heater rank. Temperature relief valves shall be so located in the tank as to be
actuated by the water in the top 6 inches (152 mm) of the tank served. For
installations with separate storage tanks, the valves shall be installed on the tank
and there shall not be any type of valve installed between the water heater and
the storage tank, There shall not be a check valve or shutoff valve between a
relief valve and the heater or tank served.
504.5 Relief valve approval. Temperature and pressure relief valves, or
combinations thereof, and energy cutoff devices shall bear the label of an approved
agency and shall have a temperature setting of not more than 210°F (99°C) and a
pressure setting not to exceeding the tank or water heater manufacturer’s rated
working pressure or 150 psi (1035 kPa), whichever is less. The relieving capacity of
each pressure relief valve and each temperature relief valve shall equal or excee
the heat input to the water heater or storage tank.
504.6 Relief outlet waste. The outlet of a pressure, temperature or other relief valve
shall not be directly connected to the drainage system.
504.6.1 Discharge. The relief valve shall discharge full size to a safe place of
disposal such as the floor, outside the building, or an indirect waste receptor. The
discharge pipe shall not have any trapped sections and shall have a visible air
gap or air gap fitting located in the same room as the water heater. The outlet
end of the discharge pipe shall not be threaded and such discharge pipe shall not
have a valve discharge piping to the disposal point. Such pipe shall be installed
in a manner that does not cause personal injury to occupants in the immediate
area or structural damage to the building.
504.6.2 Materials. Relief valve discharge piping shall be of those materials listed
in Section 605.4 or shall be tested, rated, and approved for such use in
accordance with ASME A112.4.1. Piping from safety pan drains shall be of those
materials listed in Table 605.4.
504.7 Required pan. Where water heaters or hot water storage tanks are installed in
locations where leakage of the tanks or connections will cause damage, the tank or
water heater shall be installed in a galvanized steel pan having a minimum thickness of
24 gage, or other pans approved for such use.
504.7.1 Pan size and drain. The pan shall be not less than 1.5 inches (38 mm)
deep and shall be of sufficient size and shape to receive all dripping or
condensate from the tank or water heater. The pan shall be drained by an
indirect waste pipe having a minimum diameter of ¾ inch (19 mm).
504.7.2 Pan drain termination. The pan drain shall extend full-size and terminate
over a suitably located indirect waste receptor or floor drain or extend to the exterior of
the building and terminate no less than 6 inches (152 mm) and not more than 24 inches
(610 mm) above the adjacent ground surface.