I guess that your problem is the neutral that must be loose or broken between receptacles.
Be careful about the measures you receive when you use a tester. For example, you have a lamp connected to one receptacle, and you have a broken wire between receptacles, you might perceive 120v anyway in the affected receptacle, because the light bulb -through its element- is letting pass the hot current through the neutral that goes to the next receptacle, plus you can receive a Neutral reading from the now broken Hot wire as a feedback from the following receptacle...so you have a false reading.
To have a better reading, the best is to disconnect every appliance, lamp, etc that is connected to the circuit in question.
The advice given in the prior reply right above is also correct, it might be a switch that controls receptacles B and C.
But, if no switch is controlling those receptacles, you might have the Neutral wire loose or broken between receptacles.
Sometimes the circuit runs different than we assume, and it might go through the ceiling light box as a junction place to distribute the power to the receptacles. I saw lots of houses wired that way, it is weird, but such is the way the installers did it and it's legal, this is to say, not against the NEC.
If no switch controls the receptacles, try first the removal of the nearest receptacles, not only receptacle A, one of them might have the faulty Neutral connection, even the one in the bathroom. If no fault is found in the receptacles, then the problem is bigger, it might be a junction box somewhere -like the example mentioned with the ceiling light- or a broken wire due to a nail or a screw when the drywall, floor mouding, a picture in the wall, etc was installed....this is the worst scenario.
I'll hope is just a simple problem between receptacles, try to find the direction of the main electric panel to use it as a guide of the running circuit, the nearest receptacle to the area where the main panel is located, might be the first in the circuit, this method of troubleshooting is not necessarily a rule, but works in most cases.