Blower motor have a negative pressure on the incoming side compared to a positive pressure on the downstream side. A plugged incoming side compared to a plugged downstream side makes a difference as to motor load and motor amps. The FLA, full load amps of the motor indicated on the motor is the highest amps to run, at higher amperage the motor is working too hard, at lower amps the motor is working less.
A plugged downstream usually makes the motor work less but it gets louder as the air and the fan, a forward leaning vane will fight and create noise. A rear leaning fan does not ususally overload the fan motor.
A plugged incoming cause less air to meet the fan and the fan can speed up as in a free wheel and use more amps.
These small fans are made to deliver their CFM of air within a very specific pressure or ESP, external static pressure and they must stay within their loading of CFM, and amps otherwise weird noises emanate especially if the radial fan touches anything other than air. The motors by design are not very torque producing and the fan rubbing dried leaves will cause an over load.
Be sure to clean the air vanes around the fan wheel, unbalances makes for more weird noise.